Generally, for the ENGINEERED used of masonry, it has been found that the best measure of the compressive strength (and other properties) is a prism test. It is usually conducted on a prism with a h/t of 2, but correction values have long been established and accepted.
The results of prism tests have shown that mortar has a small effect of the compressive strength of a masonry wall and compressive strengths of the masonry units controls the engineered strength. - The mortar is in a thin horizontal layer perpendicular to the load and any failure is similar to confined compression, so it has little effect.
This may not apply to your needs, but selected units could be sample to determine the approximate strength of the masonry wall. - I have seen hollow masonry prisms with a compressive strength of 5000 psi with 2000 psi mortar. For solid brick, the effects of the mortar strength would be somewhat less.
Sorry, but I do not have a copy of the subject referenced.
Dick