yfalsada

Structural
May 18, 2015
7
Hi,

I am in the process of reauthenticating the design of a villa already in progress made by a former colleague who left our company. The villa consists of a G+1 floors, with provision for a future floor.
Currently, Superstructure works up to the 1st floor columns are completed, and the contractor now is in the process of fixing the formwork for the 1st floor beams.

We have a 250mm thick in-situ concrete slab with 3-sided supports, and 1-sided cantilever. However, I am concerned that the slab does not have a backspan, as the rest of the villa is constructed using hollow-core slabs. I would appreciate your advise on how we could possibly develop the rebars sufficiently to develop the necessary rigidity in the beam/slab connection with minimal architectural changes.

Please refer to plan extract attached. Note that the beams are 500mm deep.

Thank you for your support.


 
 https://files.engineering.com/getfile.aspx?folder=c4ab6f19-293a-4446-9adc-9574418d91c3&file=V1PlanExtract.PNG
Replies continue below

Recommended for you

yfalsada said:
Consequently, the slab design is ok provided bottom rebar is increased to 16mm @ 150mm to suite ULS requirements.
So you have designed the slab to be supported by beams on three sides finally?
I would like to know exactly what solution you have finalized and the detailing too..
 

Just noticed... why is the allowable deflection so low? I would have thought half of that (L/240? twice as much).

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik
 