Sorry..I don't have the 2005 NEC at home as I type this, but the 1999 code says:
300-3(c)(1): Conductors of circuits rated 600V, nominal or less, ac circuits and dc circuits shall be permitted to occupy the same equipment wiring, enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
It seems to me that this is not a problem.
Mike