George, Here's the scoop.
For a constant air entering dry bulb temperature, the DT across a coil increases with decreasing relative humidity. This is because the coil condenses a decreased moisture (latent) load. If a coil doesn’t have to condense much moisture from the air, it can perform more sensible cooling. Sensible cooling is what we are measuring. Humidity can account for several degrees of dry bulb deviation. Therefore, on a humid day, the sensible DT reading will be lower as more of the air conditioner’s capacity is used to dehumidify. Conversely, if the relative humidity of the return air is low, the sensible DT will be higher. On the average, about a quarter of an air conditioner’s capacity is used to dehumidify at 50% relative humidity. As an example, a 4 ton air conditioning system uses about 3 tons for sensible cooling, while one ton is used to dehumidify. This sensible heat factor (SHF) should be taken into consideration when taking the dry bulb DT over an evaporator to determine airflow. The dry bulb DT could vary from about 15oF, very humid return air, to 25oF, very dry return air. The 20oF DT is assuming about 50% relative humidity return air.
The air handler formula BTU/HR=CFM x DT x 1.08 won’t work with an air conditioning coil unless a SHF is considered.
BTU/HR x SHF = CFM x DT x 1.08
Examples: If we try to determine the CFM’s using the formula for a three ton air conditioner on which we’ve taken a 20oF DT without using a SHF, we will get an erroneous answer.
36,000 = CFM x 20 x 1.08
Solving for CFM we’d get 1666.67 CFM. This indicates too much air.
Inserting a SHF of .75
36,000 x .75 = CFM x 20 x 1.08
Solving for CFM we get 1250 CFM, about the right amount of air for a three-ton system.