Imok2 - Okay I'm taking the turkey off the table till this is resolved! If you are looking at rules of thumb for sizing tonnage for residential ac units, then the guidelines in the link you provided are applicable. The link recommends the typical range of cfm per square foot for residential ac applications, which, when multiplied by square footage, and divided by 400 will give you a nominal unit tonnage. Just because your numbers work out to a nominal 5 ton unit, rated at 400 cfm/ton, this does not mean you will be circulating 2000 cfm through your residence to satisfy the load. Why? Because the circulating air flow rate required is based upon the sensible cooling loads you are trying to satisfy, which is not represented by the total unit tonnage. For instance you may have a 3.5 ton sensible load, plus assuming 1 ton latent load for moisture removal, gives you 4.5 tons and you select a 5 ton unit. But you only need to circulate enough air for the 3.5 ton sensible load occurring in the spaces, because the latent load removal occurs at the evaporator. Your 5 ton unit does not need to circulate 2000 cfm to do 5 tons of cooling, and in fact after you add the pressure drop of the cooling coil and ductwork, you will probably find the unit incapable of delivering 2000 cfm, even on it's highest blower speed setting. Rather it may be able and only needs to circulate in range of 1500-1800 cfm, depending upon cooling load and system resistance, and if you do the math this works out to an air circulation rate of 300-360 cfm per ton of installed capacity. I think there are two issues being confused here; rules of thumb for sizing equipment tonnage versus rules of thumb for actual air flow circulating rates for various applications. Hope this helps to clarify the issue. Hope all who celebrate it, have a nice Thanksgiving. cheers