Hello, I got a problem on a propeller electrical motor, the name plates of the problem are the next:
-1000 HP
- Vertical motor, it´s posible to turn it by hand.
- 780 rpm 60 hz 440 V 1260 A full load.
- The propeller is a pitch control one, but when we start the motor is on the 0 position.
Now i´ll explain the way it start, the customer used a generator runing on its nominal speed, but change the excitation of the generator doing a soft start on the motor.
It have been working till one month ago, and now when you start the motor you see:
- with a voltage of 80 V a current of 800 A, if you increase the voltage to 90 V the current go to 1180, and the speed is 180 rpm.
What do you think, I was thinking about the squirrel cage of the rotor.... but... i discoupled the flanges of the rotors and try to start and the motor start in two seconds aprox. with a peak current of 1450 A but it decrease very fast ultil 92 A. and the voltage on the generator rise from 80 to 150 V, i think due to the less current the generator have to feed.
I think if you put 1180 A during 3 minutes on a motor, with the nominal frecuency its speed will grow up more or less fast depending on the load, but always grow up, ...
please, i wait for your always nice commentaries
thanks in advance
-1000 HP
- Vertical motor, it´s posible to turn it by hand.
- 780 rpm 60 hz 440 V 1260 A full load.
- The propeller is a pitch control one, but when we start the motor is on the 0 position.
Now i´ll explain the way it start, the customer used a generator runing on its nominal speed, but change the excitation of the generator doing a soft start on the motor.
It have been working till one month ago, and now when you start the motor you see:
- with a voltage of 80 V a current of 800 A, if you increase the voltage to 90 V the current go to 1180, and the speed is 180 rpm.
What do you think, I was thinking about the squirrel cage of the rotor.... but... i discoupled the flanges of the rotors and try to start and the motor start in two seconds aprox. with a peak current of 1450 A but it decrease very fast ultil 92 A. and the voltage on the generator rise from 80 to 150 V, i think due to the less current the generator have to feed.
I think if you put 1180 A during 3 minutes on a motor, with the nominal frecuency its speed will grow up more or less fast depending on the load, but always grow up, ...
please, i wait for your always nice commentaries