I have a couple of questions. When calculating the value "d" for rebar location in a grouted masonry cell, is it common to use 1/2 the block depth? I've normally used .45 x block depth. Is that too conservative?
I've done some split-face block design before, but never played around with brick veneer. The contractor deviated from my 10" CMU design and used an 8" block with 4" brick. He is contending that the brick adds to the strength of the wall (there is an air space between.) To me, it seems that the ties only transfer the load to the block, which does all of the work. Is there a way to increase the capacity of the 8" block wall with the 4" brick?
Thanks
I've done some split-face block design before, but never played around with brick veneer. The contractor deviated from my 10" CMU design and used an 8" block with 4" brick. He is contending that the brick adds to the strength of the wall (there is an air space between.) To me, it seems that the ties only transfer the load to the block, which does all of the work. Is there a way to increase the capacity of the 8" block wall with the 4" brick?
Thanks