Ben29
Structural
- Aug 7, 2014
- 326
This is an 8" CMU fire wall that is left exposed after the demo of the end unit. It sits on a concrete basement wall below the first floor.
This wall is not laterally tied to the existing house, except for at the stair header. The existing house floor framing runs front to back. Roof truss also running front to back.
The roof of the remaining house is approximately 2ft lower than the top of the 8" block fire wall. So the plan is to remove the top 2ft of fire wall. They are most likely going to re-roof the remaining house. So I figure I could provide a detail where the top of the block wall is laterally braced by the roof diaphragm.
Do we think its necessary to tie the second floor to the block wall with tie rods. I could see squeezing in (2) ties at the rear of the house, just beyond where the stair header frames in.
This wall is not laterally tied to the existing house, except for at the stair header. The existing house floor framing runs front to back. Roof truss also running front to back.
The roof of the remaining house is approximately 2ft lower than the top of the 8" block fire wall. So the plan is to remove the top 2ft of fire wall. They are most likely going to re-roof the remaining house. So I figure I could provide a detail where the top of the block wall is laterally braced by the roof diaphragm.
Do we think its necessary to tie the second floor to the block wall with tie rods. I could see squeezing in (2) ties at the rear of the house, just beyond where the stair header frames in.