How many amps can I put on this 750kW cat? Manufacturer uses 0.8 as power factor. My 480V building is at 0.95 power factor.
750kW/0.8 = 937kVA
750kW/0.95 = 789kVA
Building Load is 1020A.
1020 X 480V X root3 x 0.95 = 806kVA
So, one guy says use the 937kVA rating because the bldg pf is .95.
The other says use 789kVA rating because the 750kW rating is based on 0.8, independent of the bldg pf.
Which is correct? Can I put the full 1020A on this cat or not?
Thanks!