So, the design engineer didn't follow the generally accepted protocol of the applicable welding code. When in doubt, direct the question to the person responsible.
It doesn't matter what profession we look at. 10% would be better off looking for work elsewhere. They don't do or can't do their job. They would rather pass the responsibility to someone else. Most enter politics at some point.
80% do enough to get by and hold on to their jobs.
10% excel by going the extra mile.
OK, I've stirred up the mud, flung stones in the direction of the glass house, in general vented my frustration. For that I apologize.
The truth of the matter is, the detail you included isn't the generally accepted way of specifying the weld size. The Engineer is suppose to specify the required weld size (joint penetration) per AWS D1.1. The Engineer does not have to specify the groove type, groove angle, etc., but the weld size is a requirement. That shouldn't be too difficult since the Engineer did specify the size of the column which means he must know the forces on the connection and thus the weld size.
Clearly, it is beyond the Engineer's capability or maybe simply he or she is too lazy to do the job.
As the fabricator's detailer, you can select from a number of prequalified joint details included in Figure 3.3 of AWS D1.1/D1.1M Structural Welding Code/Steel or a different D1.X structural welding code if applicable.
Generally, the weld size for a bevel groove with a groove angle between 60 degrees and 45 degrees is 1/8 inch less than the depth of the bevel. Again, check the details included in figure 3.3 for the specifics. The generic welding symbol is included. All you have to do is fill in the values required by the welding symbol, i.e., groove angle, bevel depth, etc.
Best regards - Al