Feg
Mechanical
- Oct 2, 2003
- 77
A customer of mine has had a motor failure on compressor, the original motor was a SIEMENS ODP IP23 500Kw 4pl B5 flanged Model 1LL3352-4HF31-Z 3.3Kv. Due to lack of funds the company is now considering the surplus motor market, one such supplier has offered a second hand MOTOR 1LL3352-4AA51Z 450kw 5000v 65Amp .84 cos 50hz KL4 40 deg max 105K SF 1.1 but reconnected. I have no experience of high tension motors but i am assuming they are talking about reconnecting the motor in delta.Can anyone confirm my thinking and will this work as i thought the voltage tolerance would be only 5 to 10 %, would they be able to use this at 3300v and what kw could be drawn from it. Any comments would be welcome on this subject.