I think I just found what you are looking for.
Take a look at page 6 of the attached pdf.
3.2.1.3 For a multi-ratio internal bushing current transformer with a maximum rating equal to the nameplate rating of the equipment in which it is installed, but which is operating on a reduced tap, the calculated equipment capability should
be reduced by the factor:
SQRT(It/In)
Where It is the reduced tap current rating, and In is the maximum current rating of the current transformer.
If information is not readily available on the continuous thermal rating factor of a bushing current transformer, the manufacturer should be consulted.