pebe,
Thank you for your continuing interest. and various suggestions.
Yes the 'user idents' are all me.
I offer the following description of the problem and my solution which may be of interest to the curious and prompt further discussion. (Apologise for referring to flow and pressure switches -- there are only flow switches).
Installation:
A domestic shower is supplied by an electric pump. The pump motor is turned on or off by two flow switches wired in parallel. One flow switch is in the cold feed to the shower head. The other is in the hot feed. The feed pipe work from the pump to the shower head is about 25 feet.
Correct operation:
User turns shower mixing valve on. Gravity induced water flow operates flow switches and turns pump on. User closes mixing valve water flow stops. Flow switch detects no-flow condition and pump motor turns off.
Actual operation:
As above until user closes mixing valve. Water flow stops. Pump stops but then proceeds to cycle on and off approximately three times a second. (Due to travelling pressure waves in the long pipe work. These waves are detected by the flowswitch(es) which momentarily close and open). Turning pump supply off and on cancels cycling and system becomes stable.
Corrective action:
Various mechanical solutions tried but to no avail.
Desired effect of cicuit
When the flow switch(es) open when the mixing valve is closed they are isolated from the control circuit for three seconds. This prevents the pump starting and allows the pressur waves to die. At the end of the period the flow switches are automatically reconnected and the pump becomes available for use once more.
Restraints:
The solution must use the installed flow switches and pump.
Electrical charateristics of plant:
Flow switches are reed switches in with series 470 ohm resistance in a common encapsulation.
Pump motor is a capacitor start and capacitor run.
Operation of circuit
Shower mixing valve opened
Normally open flow switch closes on water flow. Flow switch relay (RL4) energised. Normally open contact RL4/1 closes puts feed onto motor relay (RL3) and trigger relay (RL2). Motor contact RL3/1 closes motor starts. Trigger contact RL2/1 opens.
Shower mixing valve closed
Normally open flow switch opens on water flow stopping. Flow switch relay (RL4) denergises. Normally open contact RL4/1 opens removes feed to motor relay (RL3) and trigger relay (RL2). Motor contact RL3/1 opens motor stops. Trigger contact RL2/1 closes initiates timer. Flowswitch interlock relay (RL1) energises. Contact RL1/1 opens for approximately three seconds. At end of period RL1/1 closes and circuit ready for next operation.
Again many thanks
Bob B