51N Relay Settings for Unigrounded Systems Feeding Delta Connected Loads

Status
Not open for further replies.

bwen08

Electrical
Oct 7, 2010
28
I'm trying to find some further reference material on determining the ground relay settings for a 3 wire solidly grounded system that feeds delta connected loads. (i.e. sub-transmission feeders with Dy1 power transformers) What situations would cause sympathetic trips to occur if the ground settings were set too low other than accuracy of the CT's & relay?

Thanks!
 
Replies continue below

Recommended for you

How about single phase to ground connected loads that the field guys fail to tell you about. Or capacitor banks with fused primarys (where one fuse may blow). Or a somewhat conducting arrestor. Or leakage current from a contamated insulator. Or a primary metered customer tap.

 
Also, non-linear loads (eg. rectifiers/switching devices) causing high frequency components that flow via parasitic capacitance to ground.
 