The pictured Bussman FLS-R 500A fuse was installed in a Square D I-Line bus plug-in disconnect feeding an ABB DCS401.0500 drive (rated 408 AC amps/phase) driving a Reliance "Super RPM" 250 HP, 500V/400 FLA motor in a plastics extrusion screw application. The drive itself is protected with fast-clearing semiconductor fuses, and they were not affected.
I was not involved in the fuse replacement, and don't know which pole it was installed in, or it's specific orientation (although it is installed along the horizontal axis, rather than vertically).
For approximately two weeks before the fuse burned in half the drive would shut down approximately every two or three days. Unfortunately, instead of checking fault code(s) after shutdown the drive was power-cycled to clear the fault, and diagnostic information was lost. Since fuse replacement these "mystery" shutdowns appear to have ceased.
My best guess based on heavy oxidation on only half of the links is this fuse was leaking filler material, exposing progressively greater fuse element surface area to the air, and these oxidized elements developed higher resistance. Over time this process avalanched, and eventually the fuse dropped enough power for it to burn apart.
Does that scenario seem likely? Has anyone else seen a fuse failure like this?