May 22, 2003 #1 drax Mechanical Joined Mar 2, 2000 Messages 95 Location US Does anyone know the weight per foot of 500 MCM 3 conductor cable and amps capability? thanks in advance, Drax
Does anyone know the weight per foot of 500 MCM 3 conductor cable and amps capability? thanks in advance, Drax
May 22, 2003 #2 AFab Electrical Joined May 7, 2003 Messages 71 Location CA Approx 6.3 lb/ft, 395Amps for 90deg C Upvote 0 Downvote
May 22, 2003 #3 jbartos Electrical Joined Jan 15, 2000 Messages 6,440 Suggestion: It will vary with the cable construction. Visit http://www.generalcable.cometc. for more info Upvote 0 Downvote
Suggestion: It will vary with the cable construction. Visit http://www.generalcable.cometc. for more info
May 23, 2003 #4 Shortstub Electrical Joined Dec 30, 2002 Messages 268 Location US What is insulation type? Is it shield? Lead covered? Upvote 0 Downvote
May 27, 2003 Thread starter #5 drax Mechanical Joined Mar 2, 2000 Messages 95 Location US It is shielded underground utility cable. Upvote 0 Downvote
May 28, 2003 #6 SteveHuck Electrical Joined Jan 9, 2003 Messages 27 6.5Lbs per foot / 430A for a thhn 90C Upvote 0 Downvote