5 conductors per phase parallel run 3

Status
Not open for further replies.

MD88

Electrical
Joined
Mar 5, 2020
Messages
9
Location
CA
Hello,

I've got a 2500A, 600V run to put in, and I'd like to use 15x1c-350MCM 100% spaced as per CEC Table 1 (Canadian project). My question is what would be the optimal conductor and phasing arrangement to minimize the inductive reactance differences. Any tips or references would be much appreciated.

Thanks
 
I saw an installation years ago with a product called, as I recall, Flexi-Bus.
It was similar to a maple block system but the spacers were a composite of some sort.
A every spacer, about one meter on centres, every cable changed position, until every cable occupied each spacer position.
For 5 or 6 wide and 3 or 4 deep, and 1000 MCM cables the labour was outrageous.

Here is shown mphusky cable bus. Straight runs of cable, no change of position in the spacers.
cable-bus-inner-banner_jky0yr.jpg

Imagine mphusky Cable Bus, on steroids, with a twist!
Any savings on possible losses would take many years to pay back the extra labour.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 