What on earth is a neutral-earth link as applied to a delta configuration?neutral-earth link
Or a wye:delta transformer.You need a zigzag transformer that will provide you a neutral that you will connect through a grounding resistor. The size of this resistor will determinate the size of the zz transformer.
Thanks for your reply. If it is a solidly grounded system. What will be the size of the wye: delta transformerOr a wye:delta transformer.
The size of this resistor will determinate the size of the wye:delta transformer.
Thank you for your reply. How is the resistor calculation done and then based on this what will the transformer size if I am to use a zig-Zag transformer. Could you please share a sample calculation if you have it would be really helpfulYou need a zigzag transformer that will provide you a neutral that you will connect through a grounding resistor. The size of this resistor will determinate the size of the zz transformer.
Ohm's Law.How is the resistor calculation done
it will be a solidly grounded system to detect earth faults and the 3.7kA is on the 480V side and not on the 13.2kV side. The 13.2 kV side grid is also built by us and we are the only utility in the rural area.Wait. It sounds like you want to establish a ground on the 480 V side of the transformer? First question is why? Perhaps the ungrounded delta was chosen for a reason??
If you want to ground a 480 V system, it needs to be either solidly-grounded, or high-resistance grounded (5 A or less). Low-resistance grounding systems are not safe at 480 V. Don't do this.
The 3.7 kA of SLG fault current is presumably on the 13.2 kV side. This is more or less irrelevant for 480 V grounding due to the delta winding.
Respectfully suggest that you engage the services of a EE with experience in grounding of distributed generation systems. If the 13.2 kV system belongs to the utility, you should also discuss this with them sooner rather than later.
Good luck.
Hi All, I have a hybrid power plant with PV, Battery and DG connecting to a 13.2 kV grid via a step-up transformer. the 480V side is delta which is ungrounded, how do I size a grounding transformer? the L-G fault is 3.7kA,
thank youEach separately derived system when grounded, shall have the neutral bonded to earth at one location only.
That would be your neutral to earth link.
The transformer must withstand fault current until the system protection clears the fault. That is why a resistor is used to limit the fault current.
The resister must be in the neutral conductor of the balancing transformer.
Thanks to dpc for clarifying. Yes...400A resistor on a 480V system is no bueno. My suggestion is for a MV system.Consider the withstand time of the resistor. A 400A resistor is pretty common, having a 10 second withstand. Extended time ratings means more $$$.
Mike