480 voltage

Status
Not open for further replies.

Santaman7

Electrical
Joined
Aug 31, 2010
Messages
5
Location
US
what is the min. air gap needed to prevent 480 volt AC from arcing?
 
Scary question without more information but...

Your Dielectric Withstand Test uses 677 Vdc (or 479 Vac). If the test passes it will confirm that the smallest gap between exposed conductors in the cable is likely greater than 0.003 inches (0.08 mm). If the test fails you may have a gap less than 0.003 inches (0.08 mm). If the DWV test is done in helium then the test might detect a gap as large as 0.083 inches (2.11 mm).
 
This is for a heater bank in a oven that is going through a pass through. I am talking about phase to ground and I would also like to know about phase to phase. Is there any standard for air gaps ver. voltage? I have a probe that is about 1/8" away from ground and I do not want it to arc.
 
Post your question in the electrical forum. There are probably code required air gaps that far larger than than what you would calculate based on first principles. Why would you not use a ceramic insulator on a wire passing through a steel wall?
 
I am using a ceramic insulator, but where the probes passes throuh the wall the probes gets reall close to the fitting I have that it mounts to.
 