jbartos, it may be just a matter of terminology, but this is not the first time that you have referred to a wye-delta starter as a 'soft start'. Please note that although a solid state (soft) starter may be known as a reduced voltage starter, a wye-delta starter is not a soft start. To avoid arguing over terminology I will give my definitions and my reason for believing that they are different.
A reduced voltage starter is one that starts the motor with reduced voltage across the windings. The methods of accomplishing this include primary reactor, primary resistor, autotransfomer, part winding, wye-delta, and (of course) solid state starters.
The primary factor that distinguishes a 'soft start' from the other types of reduced voltage starters is the fact that a soft starter offers continuously variable voltage from start to full speed. Specifically, the starter begins at 0V (full frequency) and ramps the voltage up to full value (240V, 480V....) based on user selection of acceleration time. This is done using SCR's.
All other types of reduced voltage starter involve discrete steps in the voltage applied to the windings. In other words, the motor starts in steps beginning at, for example with a autotransformer starter, 65% voltage and 42% torque right away. After a fixed time delay, the starter switches to full voltage and full torque. Two steps...'half speed' and full speed. If you stand next to one starting, you will hear (and see on the ammeter) two distinct steps. It is possible for these types of reduced voltage starter to have more than two steps, but this is not common and is more costly for each step added. However, no matter how many steps you add, the result is that for each step the motor sees an step increase in voltage and as such has an inrush and a torque surge with each step.
A soft starter uses SCR's to ramp the voltage up to full value based on user settings for acceleration. The ramping of the voltage (and torque output) is continuous from 0V to full volts. If you stand next to one of these while starting, you will not notice steps in starting but will see a gradual increase in speed. This is the basis for the name "soft start".