Thanks for the information, Jeff.
OP said:
so now you have to yank a bunch of 250 foot runs of conduit off a 40 foot ceiling and replace it all with larger everything.
In Canada, these conduit runs would either have equipment bonding conductors or in some instances the conduit may serve as the bonding conductor.
Our code allows normal splices in bonding conductors but is very restrictive of splices in system grounding conductors.
The sizing criteria is also different.
In most plants we would have to run new system grounding conductors to meet code.
Hence my question regarding the effect of voltages to neutral/ground of 277V, 139V, and 139 Volts.
Your solution is the acknowledged best way to go in most instances Jeff.
However, if Keith is faced with running hundreds of feet of system grounding conductors, it may be well to investigate the usability of an alternate solution.
Another option may be to use three transformers connected as wye autotransformers. This would give 240 Volts with equal voltages from line to ground.
Bill
--------------------