The Volts per Hertz will be exceeded and the motor will saturate.
The motor will burn up long before you complete the calculations, even if your are a fast calculator.
Rated voltage = 460 Volts.
V/Hz = 7.67 V/Hz.
Safe 50 Hz V = 50 Hz x 7.67 V/Hz. = 383 Volts safe 50 Hz voltage.
Guesstimate saturation at 115% over voltage = 440 Volts, 50 Hz.
As the voltage rises above saturation the current is limited by the air core inductive reactance and the winding resistance.
You will have about 480V - 440V = 40 Volts driving current through the resistance of the motor windings.
The current will be excessive.
By now the smoke is coming out.
How accurately do you want to calculate the impending time of death?