Hi All
I have been asked to look at a job we are doing where the supply authority is upgrading the supply transformer and in doing so the system voltage is going to change from the previous 440V to the new 400V mandated by IEC standards.
The site is a hazardous area and the plant I am concerned about are some three phase induction motors which are used to pump petrochemicals.
The motors have 'Ex' ratings for use in a Zone 1 area under the IEC regulations. The motors are in the range 22-40 kW and have nameplate voltage of 415V delta. The motors are old and no manufacturer's data is available.
The reduction in system voltage from 440V to 400V, with a utilization voltage of 380V (5% max voltage drop) is going to do the following as far as I can see however I am interested in what everyone thinks:
-Increase motor current draw
-Increased draw will lead to further losses, more heat generated
-I am concerned that this increased current is outside the motor's certification however certification documents are not available
-The motor will draw higher current at rated load and hence should be derated (%30)?
This is a result of the supply authority changing the nominal system voltage to 400V. Previous voltage should have been 415 but was 440 due to oddball HV/LV transformer.
How has everyone else managed this situation, where you have an existing site where the supply is changed/upgraded and the utility has decreased the supply voltage. This is due to the change to bring the supply voltage in line with IEC recommendations.
Is it a case of ensuring the existing devices on site can operate at 380/220V? What if they cant? Surely the supply authority can't just change your voltage requiring you to replace half your devices? or submains?
I have been asked to look at a job we are doing where the supply authority is upgrading the supply transformer and in doing so the system voltage is going to change from the previous 440V to the new 400V mandated by IEC standards.
The site is a hazardous area and the plant I am concerned about are some three phase induction motors which are used to pump petrochemicals.
The motors have 'Ex' ratings for use in a Zone 1 area under the IEC regulations. The motors are in the range 22-40 kW and have nameplate voltage of 415V delta. The motors are old and no manufacturer's data is available.
The reduction in system voltage from 440V to 400V, with a utilization voltage of 380V (5% max voltage drop) is going to do the following as far as I can see however I am interested in what everyone thinks:
-Increase motor current draw
-Increased draw will lead to further losses, more heat generated
-I am concerned that this increased current is outside the motor's certification however certification documents are not available
-The motor will draw higher current at rated load and hence should be derated (%30)?
This is a result of the supply authority changing the nominal system voltage to 400V. Previous voltage should have been 415 but was 440 due to oddball HV/LV transformer.
How has everyone else managed this situation, where you have an existing site where the supply is changed/upgraded and the utility has decreased the supply voltage. This is due to the change to bring the supply voltage in line with IEC recommendations.
Is it a case of ensuring the existing devices on site can operate at 380/220V? What if they cant? Surely the supply authority can't just change your voltage requiring you to replace half your devices? or submains?