I used a Ductilator to arrive at the numbers for the pressure drop per 100 feet and the velocity. You can use a manual one or an electronic ductilator. For the duct length, I used the length you gave us and multiplied it by 1.5 (to account for any elbow, turn, etc...). Now keep in mind this is a rule of thumb for quickly calculating the ESP. If this is a critical application, you must go into more detail and account for EVERYTHING in the system. Now, you stated that this was for normal supply air. This ESP seems kinda high. You typically don't see this amount of ESP for normal supply air. For normal supply air, typically it is in the range of 0.25 to 1.00 or so. You have to be careful with the static pressure because if you specify a fan that has 3 inches of static pressure and the contractor installs a typical gauge duct for supply air, then you will have a problem. The duct will balloon and pop all the seams along with the insulation creating a problem for everyone.