Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

4" FDC Tieing into 3" Grid Main

Status
Not open for further replies.

mcarewm

Mechanical
Apr 30, 2008
13
Hey all .

I have a single riser for a mall building . I am coming off
my Grid main to feed my 4" FDC . My Drop is 4" diameter piping , My Grid Main is 3" .

do I need to up size my Grid Main to 3" ? I have checked NFPA 13 2008 8.17.2.3 ....

My Riser is 4" diameter , so I am thinking I would have to up size the 3" to 4" . But don't see anything in the Code to determine this .

any thoughts .

reference to NFPA 2008 8.17.2.3 , 8.17.2.4.1 , A 8.17.2.4.1

thanks
 
Replies continue below

Recommended for you

I would have 4" piping from the FDC to the point it contacts the grid main. You should be fine at that point.

It sounds like you have a 4" riser and 4" bulk to your grid main. So, your FDC is mimicking the automatic supply.

Remember, the FDC is just an augment to the fire sprinkler system, and not a total replacement. If you have a typical mall, you are talking about 300 - 350 gpm (less if you have a QR reduction) for a total sprinkler demand.

Travis Mack
MFP Design, LLC
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor