hrc

Electrical
Nov 8, 2001
104
OK...embarking on something new here. Figure industrial control guys would know better than the circuit engineering but I figure its a toss up.

I have several 4-20mA current loop sensors, that I need to read with a micro. First off, for a sensor to be using 4-20mA as its signaling, do you simply connect a voltage source to the sensor (most are two wire devices I guess) and then stick a 100 or 250 ohm precision resistor in series to get the voltage? This is not a hobby project so if its suggested to use a unity gain amp section prior to the A/D thats ok. I need something reliable and robust. Cost is an issue of course so not looking for a OEM device to do this, but something I can put on a board layout.
 
Replies continue below

Recommended for you

Looks like you are on the right track there, hrc.
In the PLC world we use a lot of loop powered 4-20mA devices. The device is simply wired in series with a voltage source, 24VDC is typical, and an analog input module. A 250 ohm resistor across the analog input terminals then gives you a 1 to 5 VDC input to the A/D.

If you are building your own circuit, the unity gain amp section is probably a good idea, as you will need a high impedance input to the A/D in parallel with the 250 ohm resistor. Another thing to consider would be the use of an analog optical isolator between your input and output circuits.

Hope this helps.

 
Any suggestions on an analog optical isolator? I've used digital before, but haven't really seen or heard of an optical
for analog
 
Sorry, I can't recommend anything, as I haven't been designing circuits lately. I just know from looking at circuit schematics and electronics related websites, that such things are available. They typically use an LED/Phototransister to couple the input to an output.
They are also called optocouplers. There are also isolation amplifiers available, which may be more what you need. Try searching for a existing schematic, or look at the semi-conductor websites for places like Analog Devices, Burr-Brown/TI, Fairchild, etc...
 