4-20mA to optical fiber converter
chop
Does someone knows a product that can receive some analog(4-20mA) and digital inputs, multiplex them, send them trough optical fibre and at the other end of the fiber, reconvert them in analog and digital signals.
Help will be appreciate.
Hi, can you provide more details, eg. number of channels,bandwidth, optical cable length
From point A t point B, There are 1500 meters.
I plan to install two cable of six multimodes fibers 62.5/125 microns.
I need to get from B to piont A, 4 analog signals(4-20mA) and 2 digital signals(dry contacts).
Also I need to send from point A to point B, 5 analog signals(4-20mA).
Hi, I need to know the minimum bandwidth you need for each signal. thanks
I dont know what bandwidth is needed but those signals are only for information and not for control. So a resolution of 16 bits and a one refresh per second shall be enough.
I dont know if that can help you but thanks for your help.
Hi, the speed is no problem but the 16 bit resolution is, that sort of accuracy is difficult and therefore expensive. If you can get by on 12 bits then I can probably help.
12 bits will be just fine.
Hi, drop me a line on cbarn24050@aol.com, my name is Chris.
