stason
Electrical
- Apr 4, 2010
- 34
Hello,
I am performing some simulations in PowerFactory where I energize a transformer (13 MVA, 57/10,5 kV, YNd11) on the LV side (delta side) from a 7 MVA synchronous generator (with the star point solidly grounded).
The inrush current causes 2nd and 3rd harmonics to appear in the generator's currents.
If I look at the simulated zero-seqence current of the generator, it equals zero. I figured this could not be true, since the star point of the gen is connected, which would allow the 3rd harmonic currents to flow in the gen's neutral, which they also do. Is this correct? And if it does flow in the neutral, might the ground current relay trip?
Besides, will the 2nd harmonic current in the generator make the differential relay think it could be an internal fault?
Thank you in advance!
Regards,
stason
I am performing some simulations in PowerFactory where I energize a transformer (13 MVA, 57/10,5 kV, YNd11) on the LV side (delta side) from a 7 MVA synchronous generator (with the star point solidly grounded).
The inrush current causes 2nd and 3rd harmonics to appear in the generator's currents.
If I look at the simulated zero-seqence current of the generator, it equals zero. I figured this could not be true, since the star point of the gen is connected, which would allow the 3rd harmonic currents to flow in the gen's neutral, which they also do. Is this correct? And if it does flow in the neutral, might the ground current relay trip?
Besides, will the 2nd harmonic current in the generator make the differential relay think it could be an internal fault?
Thank you in advance!
Regards,
stason