Hi all,
we've been asked to investigate fuse tripping on a compressor starter:
Compressor nameplate:
RLA: 16.8A
LRA: 84 A
Fuse:
Low-Peak
class CC
current limiting
LP-CC-30 (30A)
Contactor:
Siemens
42BF35AJ
FLA:30 A
LRA:120 A
15HP 3ph
First thing we did is hook up a power recorder to the starter, here's what we found (see atached file, with max&min rms current for 1 minute intervals);
-compressor seems to start at least 30 times per hour, for 12 consecutives hours (starting 2008-10-19 @ 17:04:33).
-see blown fuse seems to happen : 2008-10-20 @ 04:44:33
-average RLA: 12 A
-average LRA: 60 A
MY QUESTION IS: can fuse operation be caused by too many consecutives starts? I2t making fuse operate maybe?
We also observed contactor wearing very fast...any comments on that?
Thank you