303kV/7.2 kV station service transformer

Status
Not open for further replies.

jacob13

Electrical
Nov 11, 2005
8
How to get auxiliary power for 500kV switchyard which does not have any transformer - just breakers and disconnects? Can we buy 300kV/7.2kV, ~300KVA single phase transformers? Any another ideas will be appreciated.

 
Replies continue below

Recommended for you

Bring in another service from the local utility distribution system. If necessary for reliability, back it up with a small diesel generator. That was the cost effective solution for one of our clients.
 
The problem we cannot make a 500KV 300KVA power tarnsformer is the minimum conductor size required.Minimum rating will be atleast 20 MVA to get mechanically reliable HV winding. Otherwise it will become a voltage transformer.It is not good to compromise the integrity of 500 kV circuit by means of such a small unit feeding station.
 
Jacob13,
In the utility I work with, when MV supply is not available nearby, we use small SF6 transformers with nominal voltages 400 kV /0.4 kV and rated power 125 kVA (single phase unit). Actually, as prc said, they look more alike to voltage transformers rather than power transformers. Note that they can include a disconnector inside the "tank".
You can find attached a brochure from one major manufacturer; I'm sorry but i didn't manage to find it in English.


Si duri puer ingeni videtur,
preconem facias vel architectum.
 
 http://www05.abb.com/global/scot/scot245.nsf/veritydisplay/34ba9c10cde9057bc12577f8004ca4de/$file/BR_HV-TIP(IT)B_2GJA708454-1012.pdf
Thanks for the information, bit they do not have 500kV voltage class.
 