Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

3-winding transformer impedance at extreme taps.

osizer

Electrical
Joined
Apr 11, 2025
Messages
4
Location
EU
I have the following data for a 3-winding transformer

S = 350/350/100 MVA (HV/LV/TV)
U = 410/230/36 kV (HV/LV/TV)
OLTC range: +/-12x1.5% located at HV side
Z(HV-LV) nominal tap = 13% @350
Z(HV-LV) max. tap = 14% @350
Z(HV-LV) min. tap = 13% @350

Can any transformer expert determine the ratio value corresponding to an impedance of 14%? Will it correspond to 483.8/230 or perhaps 336.2/230?

Logic tells me that the 14% will correspond to 483.8/230, due to the greater number of turns, but why then is the impedance for the minimum tap equal to the rated impedance?
 
Maximum tap means the highest voltage tap (usually No1 tap), i.e., 483.8/230 kV
 

Part and Inventory Search

Sponsor

Back
Top