Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JStephen on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

3 Way control valve

Status
Not open for further replies.

MagicJS

Mechanical
Joined
Dec 21, 2004
Messages
13
Can a three way control valve between supply & return headers also be used as a differential bypass?

Do you need custom controls or does someone make a valve like that?

Thanks.
 
Is this a Primary Only system or Primary + Secondary piping

2 way valve (instead of 3-way valve) may be used in the bypass pipe with a pressure sensor modulating this valve

This method is usable when the load control valves are of 2-way type and that the pumps are of constant speed type. Again, this will not save pump energy since pumps alwaysseems the same flow. Also there is no reduction in Head seen by pump since the head is used up in ovecoming balancing valve in bypass pipe.

Can give more info if you say the purpose of this by pass planned by you

 