I inherited this project from an engineer who left the firm, so I'm picking it up cold.
A quick overview of the system:
268 bed hostel, 3 storeys. 28000 litre cold water storage tank on third floor, heat pumps on a roof slab, 2x 6000 litre hot water storage tanks in the same plantroom as the cold water tank. The whole system is pressurized from the booster pump drawing from the tank. Pump is on a VSD, duty of ~ 450 l/min @ 3.5 bar, but is controlling the pressure at 4 bar after some complaints about water pressure - the pump cycles quite drastically - shuts on and off again about every 10-20 seconds.
The hot water reticulation is OK - the system is not balanced wonderfully, but there is enough draw-off that it seems to work OK. - I would have preferred a more balanced system, but the contract is over so we can't install thermostatic valves now.
The system seemed to be running decently - although apparently the plumber received a couple of call outs that we were not informed of. Then a power failure happened and the hot water circulation pumps burnt out when the power came back on.
The system wasn't designed with a power failure in mind, and the course of action was to manually open the bypass valve, this caused the problem that there was no water, and students still opened the taps (wanting water) and letting air into the system. Once the power came on, the circulation pumps were running dry and burnt out.
About a month ago the manual bypass valve was replaced with a non-return valve and the pressure reducing valves were set 3 bar. The idea was that the municipal main water pressure would take over in case of a power failure.
Since that "fix" was implemented, there are complaints about the water temperatures in the showers fluctuating suddenly and scalding the students.
I need to figure out why?
I am inclined to suspect the pump because of the cycling and I don't think it is being controlled well by the VSD, but surely that will provide fluctuations in pressure, but the balance should remain constant.
Another theory that I have is that there might be a blockage in the cold water lines, which effectively reduces the diameter of the line, and when there is additional cold water drawoff, the cold water line is affected too heavily and the shower becomes unbalanced.
Any other theories?
Kestell Laurie
South Africa
I inherited this project from an engineer who left the firm, so I'm picking it up cold.
A quick overview of the system:
268 bed hostel, 3 storeys. 28000 litre cold water storage tank on third floor, heat pumps on a roof slab, 2x 6000 litre hot water storage tanks in the same plantroom as the cold water tank. The whole system is pressurized from the booster pump drawing from the tank. Pump is on a VSD, duty of ~ 450 l/min @ 3.5 bar, but is controlling the pressure at 4 bar after some complaints about water pressure - the pump cycles quite drastically - shuts on and off again about every 10-20 seconds.
The hot water reticulation is OK - the system is not balanced wonderfully, but there is enough draw-off that it seems to work OK. - I would have preferred a more balanced system, but the contract is over so we can't install thermostatic valves now.
The system seemed to be running decently - although apparently the plumber received a couple of call outs that we were not informed of. Then a power failure happened and the hot water circulation pumps burnt out when the power came back on.
The system wasn't designed with a power failure in mind, and the course of action was to manually open the bypass valve, this caused the problem that there was no water, and students still opened the taps (wanting water) and letting air into the system. Once the power came on, the circulation pumps were running dry and burnt out.
About a month ago the manual bypass valve was replaced with a non-return valve and the pressure reducing valves were set 3 bar. The idea was that the municipal main water pressure would take over in case of a power failure.
Since that "fix" was implemented, there are complaints about the water temperatures in the showers fluctuating suddenly and scalding the students.
I need to figure out why?
I am inclined to suspect the pump because of the cycling and I don't think it is being controlled well by the VSD, but surely that will provide fluctuations in pressure, but the balance should remain constant.
Another theory that I have is that there might be a blockage in the cold water lines, which effectively reduces the diameter of the line, and when there is additional cold water drawoff, the cold water line is affected too heavily and the shower becomes unbalanced.
Any other theories?