Hi,
Normally MV & HV circuit breakers have 3 and 1 sec fault duration rating. If a CB has a 31.5kA rating for 3sec, is it correct to consider that it can withstand 31.5kA x 1.732 for 1 sec as derived from the formula used for cables (I2t = constant)? Will this formula apply to circuit breakers?
My initial thought is that CBs are type-tested only for the rated fault current at its rated duration. My fear is that a 31.5kA-3s CB may not withstand 54kA fault for 1 sec. Even though normally the CB are designed to trip faster than 1 sec, I don't think it is prudent to use 31.5kA CB in a system with 50kA calculated fault current. Hoping to hear any views on this issue.
Normally MV & HV circuit breakers have 3 and 1 sec fault duration rating. If a CB has a 31.5kA rating for 3sec, is it correct to consider that it can withstand 31.5kA x 1.732 for 1 sec as derived from the formula used for cables (I2t = constant)? Will this formula apply to circuit breakers?
My initial thought is that CBs are type-tested only for the rated fault current at its rated duration. My fear is that a 31.5kA-3s CB may not withstand 54kA fault for 1 sec. Even though normally the CB are designed to trip faster than 1 sec, I don't think it is prudent to use 31.5kA CB in a system with 50kA calculated fault current. Hoping to hear any views on this issue.