3 Phase Voltage Drop - Wye vs. Delta Feeder to Panel 1

Status
Not open for further replies.

djr3203

Electrical
Aug 3, 2011
57
I was under the assumption that for calculating voltage drop on a 3 phase, 4 wire (Wye) feeder from a distribution panel to a panel you only take into account the 1-way distance from the distribution panel to the panel because the assumption is the loads are balanced resulting in no current on the neutral to produce a voltage drop. I was under the assumption that this is the same for a 3 phase 3 wire (Delta) feeder from a distribution panel to a panel.

I was in a discussion today where someone said you do take into account the return distance on a wye feeder but not on a delta feeder. I disagreed, but taking a closer look at my voltage drop calculator, I realized the voltage drop was slightly different for a 3 phase 3 wire than a 3 phase 4 wire feeder. The interesting thing is that my calculator comes out with a slightly higher voltage drop for the 3 phase 3 wire than the 3 phase 4 wire. So I still think I may be correct? Anyone know why the voltage drop for a 3 wire feeder would be slightly more than a 4 wire?

Thanks for the input.

DJR
 
Replies continue below

Recommended for you

Does your calculator assume the same power factor in both cases? Wye sourced circuit with no current in the neutral is indistinguishable from a delta sourced circuit.
 