Hi, I´m working with motor commissioning, my doubt is: when I measure the phase-current of a 3 phase assincronous motor, I got differences in order of 2% between the value of current of one phase and other, when can I say that the system is unbalanced, and which are the risks that I have working on a unbalanced system

Thanks
 

2% unbalance current is probably OK, and may be caused by voltage unbalance or something like stator-winding dissymmetry.

Search this site for a fair amount of discussion on the matter, using keywords “ unbalance “ and “ imbalance “.
 
Hello Freshsurfer,

See also thread237-70765 "how to calculate kW losses in an unbalance motor". This may provide you with additional useful information.

Regards,
GGOSS
 