Not being a mechanical guy, I'd guess that you have some difference in flow restriction that is accounting for that difference in percentage, 2 of the fans have more restriction that the 3rd, probably additional bends etc..
Assuming that you mean percentage of speed, you most likely have this scenario:
2 fans at 60% speed = 200HP * .216 = 43.2HP total
2 fans at 42% speed = 200HP * .074 = 14.8HP
1 fan at 40% speed = 100HP * .064 =
6.4HP
21.2HP total
You will have more losses in the 3 motor scenario, but not as much as the additional savings. For argument's sake, let's say your throughput losses are 5% at 60% speed, and 9% at 40% speed (these are somewhat typical loss values). Input power draw then becomes:
2 fans @ 60% speed = 43.2HP / .95 = 45.5HP
3 fans 2 40% speed = 21.2HP / .91 = 23.3HP
Higher loss percentages, but still far less power consumed.
You will have more maintenance required by running all 3 motors continuously as opposed to alternating them to even out the wear and tear, but that is somewhat offset by the reduced loading on the motors. Overall, you still have the ability to accept the higher power consumption when servicing one motor, but you get to take advantage of the lower overall power draw on a continuous basis.
By the way, check to see if your VFDs have a kW output reading on the display, or at least the ability to send the kW value to the analog output as a 0-10VDC signal. Most of them do. Then all you would need is a meter to read the voltage on that signal to get the kW.