THD
Electrical
- May 18, 2002
- 21
We have had issues starting a 3.6MW Squirrel Cage motor with an 85% auto transformer tap. The inrush current is higher than the DOL inrush! We measured the inrush as 1050A with a 15% volt drop. The DOL inrush should be around 850A with a lower volt drop. The manual shows a 1140A inrush for DOL but thats obviously for infinite bus starting. We dont have infinite bus as we are starting at the end of a long 70mm2 ohead line. We are also using 5KVAr of caps to help boost the voltage as the motor starts (start banks). The caps switch out when the motor is up to speed. We were expecting a 20sec start up time for a 85% voltage start. What could be causing the inrush to be higher than that expected for DOL?
Kevin Bosch
Rainbow Technologies
Kevin Bosch
Rainbow Technologies