Yes, thankfully builders around here are used tonl framing everything around here with structural beams. Most other engineers in our area show it the same way so it isn't a fight.
Most homes built earlier than 1980 in our area are conventionally framed. To this day I have never seen one of these roofs without a "flaw". Typically, at least one (usually more) is present:
1) ceiling joists perpendocular to rafters in some area without additional rafter ties
2) rafter tie to ceiling joist occurs only every 3rd rafter and connection only has a few nails
3) one side of the ridge is partially vaulted but no consideration to the fact that the rafter tie no longer runs plate to plate
4) purlins are overspanned and only have braces at perpendicular partition walls rather than closer spacing required.
5) ceiling joists are not properly connected at splice location
6) no structural support at hip / ridge intersection.
7) collar ties are spaced too far apart.
8) at prulin brace locations no consideration given to impact on floor loading below for concentrated load.
Because these are so common I'm nevervous about contractors properly installing conventional framing. Less opportunities for error with structural ridge. As we don't have snow loads these roof defects tend to perform "OK". Areas with higher snow loads I assume can't get away with these errors and may have them less frequently (I hope at least)