I'm troubleshooting a late 50's generation delta connected 2400Vac engine blower motor. I recorded FLA of Aph=23 Bph=41 Cph=41. I thought the megger tests would indicate an insulation problem but all results were 3.5G ohm-4.1G ohm. PI is 1.1.
The motor is direct coupled to the generator windings. The phase voltages are balanced. The motor has nearly 100k hrs of operation.
Any recommendation? I plan on a winding resistance test.