calvinandhobbes10
Structural
- Feb 14, 2011
- 106
Curious--- for those of you who take advantage of the 25% reduction in seismic overturning effects prescribed in ASCE 7-10 12.13.4, do you also apply this force reduction to the sliding check? In my experience sliding is often the controlling design check these days. I understand it reads "overturning effects", however I think there's a case to be made for sliding being lumped in with it---if a shearwall is a vertical cantilever with a fixed base, you have two reactions, M and V, due to the seismic force applied. I could make a case that both M and V are reactions of the "overturning effects".
Also, have any of you ever heard of a one-third increase in the sliding friction coefficient under transient loads? E.g., 0.35 turns to 0.467 under seismic check? I have a geotech report that mentions this, first I've encountered.
Also, have any of you ever heard of a one-third increase in the sliding friction coefficient under transient loads? E.g., 0.35 turns to 0.467 under seismic check? I have a geotech report that mentions this, first I've encountered.