bnauman

Mechanical
Aug 18, 2004
1
Up front; I know enough to be dangerous, which is why I'm here.

I have a temp contoller that I'd like to use with a SSR to control the power to a heating element. This project is on the budget plan, so I was looking at e-bay for most of my components. Most of the relays I've seen there are rated for 240VAC at some X number of amps. Is there any reason why a relay would not work with a 110VAC load (heater)?
 
Replies continue below

Recommended for you

Most SSRs will work. But some of the heftier ones have auxiliary circuitry that may or may not be satisfied with the 110 V. They are then usually marked with a voltage range. Like 160 - 250 V AC or similar.

I see no reason why you shouldn't try. You cannot set anything on fire if you keep gaugues up and temperatures down (heat-sink!).

Gunnar Englund
 
I agree with skogsgurra it won't normally be any problem.
 