24" Valve Anchoring? 1
khu
25
I'm working on a site project with our state DOT. On the project, there is a pond supplying water to the fire suppression systems in the buildings. There is a 24" transfer line between a pump building and the fire pond. In that line there is a 24" gate valve. The DOT designer included the State's standard detail which shows for valves over 12", a 4" concrete bearing pad is required.
Would there be any need to anchor that valve to the pad? The detail shows no anchoring, just the valve sitting on the pad.
Shouldn't be - just park the valve on the slab. The less anchors the better.
I figured this, but wasn't sure. I've never seen valves anchored, but the Contractor was asking for an anchoring detail for the valve to the slab.
The answer depends on how the piping will be installed.
If you are using piping materials with non-restrained joints, including with gaskets, it is necessary to provide anchors for the valve, to prevent pull-out of the joints.
If the piping has mechanical joints, they you will not need anchors for the valve.
bimr said:
The answer depends on how the piping is installed.
It's all butt-fused HDPE.
If the piping is buried then a valve anchor is not necessary. If the piping is installed on the ground surface, then you need valve anchors.
Big valves have lots of inertia. :)
It's not the weight. More the resulting velocity.
A black swan to a turkey is a white swan to the butcher ... and to Boeing.