You may want to double check your information.
A "wild" B phase is more common than a grounded B phase although both exist.
With a wild leg system, phase A and phase C will measure 120 volts to ground, (One transformer center tap is grounded.), B phase will be 208 volts to ground.
Both systems may be either open or closed delta, but the wild leg system is often used on open delta.
There are issues with peak reverse voltages across the internal components of drives, that hopefully some of the drive gurus will address.
respectfully