itsjackma
Electrical
- Dec 18, 2013
- 1
a contractor measured 3 1p-208v circuit breakers' loads to be 1A, 2A, 3A. the total load of all 3 breakers is 1248VA. if we are to change these loads into 1P-120V circuit breakers phase A becomes 3+1=4A, B becomes 1+2A=3A, C becomes 2+5A=, for a total of 12A. how did the load all of a sudden become 1440VA? the load VA cannot just magically increase when we change from 208V single phase to 120V single phase right? thank you all for your help.