A customer has a 3-ph 200hp motor rated 440V. The customer is fed from 3-167 kVA transformers at 277/480V. Full Load Amps of motor is 257A and he does not have info on Locked Rotor Amps or Letter Code. The customer claimed the 200 hp motor did not have enough torque to get past the initial startup and he measured the intial current to peak at only 1400A. If the locked rotor amps is ~6 times the FLA then the inrush current should be at ~1542A. Does anyone know why this motor is not starting?
A potential factor is the operating tolerance(+-10% of 440V) of the motor is not completely within the tolerance of the operating limits of the utility (+-5% of 480V). If the supply voltage is above the voltage tolerance of the motor, wouldn't the motor still start but will overheat and burn? Thanks.
A potential factor is the operating tolerance(+-10% of 440V) of the motor is not completely within the tolerance of the operating limits of the utility (+-5% of 480V). If the supply voltage is above the voltage tolerance of the motor, wouldn't the motor still start but will overheat and burn? Thanks.