Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations 3DDave on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

2009 IBC Table 2308.9.6

Status
Not open for further replies.

ToadJones

Structural
Jan 14, 2010
2,299
Can someone shine a little light on IBC table 2308.9.6.
Does this table apply to residential construction?
What loads are used to make this table?
Is it based on strength? deflection?

 
Replies continue below

Recommended for you

The loads are per section 2308.2.1.

Garth Dreger PE
AZ Phoenix area
 
2308.2.1 in the 2009 IBC is "Basic Wind Speed greater than 100 mph"
???
 
Section 2308 is for conventional light frame construction, with the limitations for the table you are concerned about set forth in section 2308.2.3, giving the max dead at 15, and the max live at 40.

So, residential floor with no topping slab for Table 2308.9.6.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
Sorry it is section 2308.2 Limitations

Garth Dreger PE
AZ Phoenix area
 