Suggestion: Please, would you provide more information regarding the power distribution unit, whether or not it is three phase 4-wire or single phase 3-wire. Normally, if your run two conductors and ground to each receptacle, not considering a split duplex receptacle, the neutral to this receptacle is supposed to be 100% only, not 200% or more. The larger neutrals come into picture for three-phase panels or on the single phase three wire systems (240/120V single phase, 3-wire panel). If you post the panel nameplate data, then it will be easier to provide the correct answer.