Ralph...your post is right on for BS/IEC/AS, etc... standards. In the IEEE/CSA world, all protection CTs have an accuracy limiting factor of 20. I.e. C400, C800. They specify that the CTs maintain a 10% accuracy to to 20 times rated current at a given burden. Instead of a burden listed in VA or ohms directly, they list the accuracy limiting voltage, i.e. 200, 400, 800 V. This can be transformed to a burden, i.e. 800V is the same as an 8 ohm burden, assuming a 5A rated secondary. 5A x 20 x 8 ohms = 800 V.