I have a requirement to place plug-in 1.08 kW, (115v) hotplates throughout a resturant. The challenge is to avoid adding another electrical panel and more breakers I hoping to place two plug-in hotplates on there own single, 120v/20 amp receptacle with those two single recepticles connected on the same 25 amp breaker.

So the question is can a 20 amp receptacle be placed on a 25 amp overcurrent protected circuit?
 
Not the correct forum, but...

Absolutely not... no more than you could use an undersized wire on such a circuit.


Dan - Owner
Footwell%20Animation%20Tiny.gif
 
Not legally in either the US or Canada.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 